    RE: Missing alarms

    Hi Regin,
    This may be obvious, but have you updated the alarm servers, and the citect
    station with the latest version of your project which you've been doing your

    checking from?
    Double check your variable tag that drives your 'new' alarm. Make sure it
    is declared correctly to the right type of variable, and that the address
    pointing to your IO device is correct to the address you expect inside your
    IODevice. Perhaps compare another alarm/variable tag that you know works to
    your new ones.
    Do you use 'area' to distinguish who can see which alarms across your site?
    Perhaps you've not set the 'area' number correctly for your new alarms? You
    must be logged into that area to be able to view those alarms.
    When you add a new database element in Citect, you need to delete the
    'almsave.dat'files from your alarm servers to ensure correct operation of
    your alarm and 'summary' lists, otherwise you may get different
    alarms/events triggering when a certain alarm or event is generated. when
    the opportunity exists, shutdown both alarm servers, delete the file, and
    re-start. You will lose all of the 'cached' summary list entries when you
    do this.
    Hope some of this helps you.
    Julian Kovacic
    OneSteel Whyalla
    South Australia
    julianandjoanne@yahoo.com.au

    -----Original Message-----
    From: Citect Users Email List []
    Sent: Thursday, 25 March 2004 12:24 AM
    To: Citect Users Email List
    Subject: Missing alarms

    Can anybody tell me why a number of alarms does not appear in the alarm
    list?
    I have about 20 digital alarms which are set up correctly, and the value are

    changed to '1' but for some reason they does not appear in the alarmlist.
    Aother alarms in the same category does display properly. Im using 5.42
    Best Regards,
    Lyngsoe Systems A/S
    Regin J Madsen
    Software Engineer
    - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
    Lyngsø Allé 3
    DK-9600 Aars
    Denmark
    Direct: + 45 96 980 976
    Phone: + 45 96 980 980
    Fax: + 45 98 622 394
    E-mail: rjm@lyngsoesystems.com
    Web: www.lyngsoesystems.com
    - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
    Lyngsoe Systems is a global provider of logistics solutions designed to
    significantly improve your quality of service and competitive power


View as RSS news feed in XML
Powered by Community Server, by Telligent Systems